The virtual PLC runs a Structured Text (ST) program directly in the browser. Write the program in the PLC editor, then click Deploy and Run. Once per simulation tick, it reads the twin’s PLC signals, runs your logic and writes the outputs. You need no separate build or installation. The browser compiles the program when you deploy it.
Use it to test control logic against the twin before the real controller exists, to try out a sequence quickly, or to teach PLC programming on a running machine. For simple sequences without code, use logic steps instead.

Quick start
Section titled “Quick start”- Switch to the Planner workspace and click the PLC Editor button in the tool bar on the left.
- If the model already has PLC programs, the editor opens the first one. Otherwise the model gets a node PLC with a PLC Program component and a short template program.
- Edit the program. Syntax errors are marked while you type.
- Click Deploy to compile and load the program. Compile errors and unknown signals appear as markers in the code.
- Click Run. The status changes to running and the watch list shows live values.
The editor stays open when you change workspaces, and the PLC keeps running while you watch the plant. Only the Viewer workspace hides the editor.
Editor controls
Section titled “Editor controls”| Control | What it does |
|---|---|
| Deploy | Compiles the program and loads it with fresh timers, counters and memory |
| Run / Stop | Starts cyclic scanning, or stops it. Stop keeps all values, so Run continues where it stopped |
| Step | Runs exactly one scan, useful while the simulation is paused |
| Reset | Resets timers, counters and memory to their start values |
| Status | stopped, running or error. Hover the status to read the error message. The scan time in ms is shown next to it |
| Insert signal | Opens a signal browser and inserts the chosen signal into the program (see below) |
| Export / Import | Saves the program as a .st file, or loads one |
| Program list | In a model with several programs: every program in scan order with its state and scan time. Pick one to edit it |
The watch list below the code shows the current values of all signals the program uses and the outputs of its timers and counters, such as tDwell.Q or cycles.CV. Hover a name in the code to see its type, value and signal.
Connecting signals
Section titled “Connecting signals”A program reaches the twin through a VAR_EXTERNAL block. By default the variable name is the signal name:
VAR_EXTERNAL SensorInFeed : BOOL; (* reads the signal SensorInFeed *) ConveyorStart : BOOL; (* writes the signal ConveyorStart *)END_VARTo use a short name in the program, or a signal whose name is not a valid ST name (for example FG01_P_Camera.bReady), add the signal name as a comment:
VAR_EXTERNAL ProbeDown : BOOL; (* @signal: FG04_Y_AxisZ_WorkPos *)END_VARInsert signal writes these lines for you. Search for a signal and select it. The editor adds a declaration with a short name and the @signal comment, then inserts the name at the cursor. The browser lists signals from the model and a connected realvirtual CONNECT interface. Each entry shows direction, type and address.

When you deploy:
- A signal the program only reads but that does not exist gets a warning and reads
FALSEor0. Usually the name has a typo. - A signal the program writes but that does not exist is created under
PLC/<name>.
Example: station 4 of the welding station
Section titled “Example: station 4 of the welding station”This program for the Laser Welding Assembly Station moves the probe of the curling check down and up and switches the yellow tower light on after five cycles:
PROGRAM MainVAR_EXTERNAL ProbeDown : BOOL; (* @signal: FG04_Y_AxisZ_WorkPos *) ProbeUp : BOOL; (* @signal: FG04_Y_AxisZ_HomePos *) ProbeIsDown : BOOL; (* @signal: FG04_Y_AxisZ_InWork *) ProbeIsUp : BOOL; (* @signal: FG04_Y_AxisZ_InHome *) TowerGreen : BOOL; (* @signal: SignalTower_Green *) TowerYellow : BOOL; (* @signal: SignalTower_Yellow *)END_VARVAR seq : INT; tDwell : TON; cycles : CTU;END_VAR CASE seq OF 0: ProbeUp := FALSE; ProbeDown := TRUE; IF ProbeIsDown THEN seq := 1; END_IF; 1: tDwell(IN := TRUE, PT := T#1s); IF tDwell.Q THEN tDwell(IN := FALSE); seq := 2; END_IF; 2: ProbeDown := FALSE; ProbeUp := TRUE; IF ProbeIsUp THEN seq := 3; END_IF; 3: tDwell(IN := TRUE, PT := T#2s); IF tDwell.Q THEN tDwell(IN := FALSE); seq := 0; END_IF; END_CASE; cycles(CU := seq = 3, R := FALSE, PV := 5); TowerGreen := TRUE; TowerYellow := cycles.Q;END_PROGRAMThe welding station’s own program Station04 drives these outputs too. To try the example there, pick Station04 in the program list and Stop it first, then deploy and run your program.
Virtual PLC and logic steps
Section titled “Virtual PLC and logic steps”The virtual PLC runs independently of a model’s logic steps. If both write the same outputs, they conflict. You must resolve this in the model yourself.
Several programs
Section titled “Several programs”A model can carry several PLC programs, with one PLC Program component per node. Like blocks in a real PLC, these can represent individual machine units. All programs scan in the same tick, one after another, as set by their Order field. An output written by two programs is reported as a conflict.
The Laser Welding Assembly Station is controlled this way: eleven programs under the node PLC_Programs — operating modes, transport, the two lifts, the buffer, the entry and the five stations.
Simulation or PLC mode
Section titled “Simulation or PLC mode”A program can read the model’s control mode through the read-only system variable RV_SimulationMode:
VAR_EXTERNAL RV_SimulationMode : BOOL; (* TRUE = Simulation, FALSE = a real PLC owns the outputs *)END_VARST programs keep scanning in both modes. To stop writing when a real controller takes over, you check RV_SimulationMode in the program and write nothing while it is FALSE. When the model switches to PLC, running programs that use this variable get a one-time reset of their outputs to their start values. The welding station’s programs all work like this.
A program without this check keeps writing in PLC mode and works against the real controller. Stop it before you connect one.
For logic steps, you set Active on each logic root: Always, Connected, Disconnected or Never. Only roots set to Disconnected stop in PLC mode. Editor-created containers run Always. When a root stops, the outputs it owns return to their start values.
Language
Section titled “Language”The PLC supports a practical subset of IEC 61131-3 Structured Text. Keywords are not case-sensitive; comments are written (* … *) (they cannot be nested) or // …. Everything outside the subset is reported as an error with line and column when you deploy. The compiler never runs something other than what you wrote.
Beyond the program itself you can call built-in functions, write your own FUNCTION and FUNCTION_BLOCK in a PLC Library, and command axes with PLCopen motion blocks.
What works
Section titled “What works”| Area | What you can use | Example |
|---|---|---|
| Program | One PROGRAM … END_PROGRAM per PLC Program component, with VAR, VAR CONSTANT and VAR_EXTERNAL blocks | PROGRAM Main … END_PROGRAM |
| Your own functions and function blocks | FUNCTION and FUNCTION_BLOCK with VAR_INPUT, VAR_OUTPUT, VAR_IN_OUT and VAR, kept in a PLC Library and usable in every program of the model. See Function Blocks & Libraries | FUNCTION_BLOCK Gate … END_FUNCTION_BLOCK |
| Variables | One name per line; types BOOL, INT, DINT, REAL, TIME or a function block (standard, your own, or a PLCopen MC_ block) | speed : REAL; |
| Start values | A value after :=. It must be a fixed value: numbers, constants and + - * / MOD of them | count : INT := 5; wait : TIME := T#2s; |
| Constants | VAR CONSTANT with a value. Constants cannot be changed. Use them in calculations, as CASE labels and as FOR limits | MAXP : INT := 10; |
| Function block start inputs | Start values for the inputs of a timer or counter | tDelay : TON := (PT := T#2s); |
| Numbers and times | 123, 1.5, 1.5E2, 16#FF, TRUE, FALSE, T#2s, T#500ms, T#1m30s | T#1m30s |
| Assignment | :=. A smaller type fits into a larger one (INT, DINT, REAL) | d := i; |
| Decisions | IF / ELSIF / ELSE; CASE on INT / DINT with single values, lists, constants and ELSE | CASE s OF 1, 2: x := 1; ELSE x := 0; END_CASE |
| Loops | FOR … BY, WHILE, REPEAT … UNTIL | FOR i := 1 TO 10 DO … END_FOR |
| Leaving early | EXIT leaves the innermost loop. RETURN ends the scan; outputs are still written | IF done THEN EXIT; END_IF; |
| Function block calls | Inputs with :=, outputs with =>, all by name | tDelay(IN := a, PT := T#1s, Q => ready); |
| Functions | Built-in functions such as ABS, MIN, MAX, LIMIT, SEL, MUX, SQRT, SIN, EXPT, TRUNC and the conversions <S>_TO_<T>, by position or all by name. See ST Functions | y := LIMIT(0.0, x, 100.0); |
| Reading blocks | Inputs and outputs of a block instance | tDelay.Q, cnt.CV |
| Calculation | + - * /, MOD, minus sign. Integer division cuts off the decimals | r := 7 / 2; gives 3 for INT |
| Comparison | = <> < <= > >= | IF level >= 80 THEN |
| Order of operations | Strongest first: brackets, function call, NOT and minus sign, * / MOD, + -, < > <= >=, = <>, AND, XOR, OR (IEC). NOT and the minus sign bind stronger than * and comparisons; for powers use EXPT | ok := x = a < b; means x = (a < b) |
| Logic and bits | AND OR XOR NOT: logical on BOOL, bitwise on INT / DINT | mask := flags AND 16#00FF; |
| Shifting | SHL, SHR, ROL, ROR with value and number of bits | x := SHL(1, 3); |
| System variables | RV_SimulationMode and RV_FirstScan, read-only | IF RV_FirstScan THEN … END_IF; |
Not supported
Section titled “Not supported”The compiler reports each of these as an error instead of running something unexpected.
| Not supported | Instead |
|---|---|
Strings and text (STRING, 'abc') | Use numbers or signals |
Arrays (ARRAY[0..3] OF INT) | One variable per element, or a CASE |
Structures, enumerations, TYPE | Separate variables; constants with CASE for named states |
Other data types such as WORD, DWORD, BYTE, LINT, UINT, LREAL, DATE | INT or DINT with bit operations |
More than one PROGRAM in one program text | One PLC Program component per PROGRAM |
Standard functions not listed in ST Functions (such as string, date or MOVE functions) | Write the calculation with IF and arithmetic |
| Recursion (a function or block that calls itself, directly or through others) | Use a loop |
MC_ blocks inside your own FUNCTION_BLOCK | Declare them in the PROGRAM |
CASE ranges (1..5:) | A list (1, 2, 3:) or IF x >= 1 AND x <= 5 |
Several names in one declaration (a, b : INT;) | One declaration per variable |
VAR_INPUT, VAR_OUTPUT, VAR_IN_OUT in a PROGRAM; VAR_GLOBAL, RETAIN, PERSISTENT, AT %IX0.0 | VAR_EXTERNAL for signals; inputs and outputs belong in a FUNCTION_BLOCK. Nothing survives a cold start |
Typed or based numbers (INT#5, 2#1010, 8#17) | 16# hex or decimal |
Function block calls without names (t(TRUE, T#1s)); functions may be called by position | t(IN := TRUE, PT := T#1s) |
Setting a block input directly (t.PT := T#1s;) | Pass it in the call |
Start values that depend on variables, or on a VAR_EXTERNAL | Set the value under IF RV_FirstScan THEN |
**, TIME * number, MOD on REAL, CONTINUE, GOTO | EXPT for powers; otherwise rewrite with *, IF |
Mixing BOOL and INT in AND, OR, XOR, NOT | Compare first: (n <> 0) AND b |
Converting a larger type into a smaller one by assignment (DINT to INT, REAL to INT) | Convert explicitly: REAL_TO_INT, DINT_TO_INT or TRUNC |
Overflow wrap-around of INT / DINT | Not performed, see below |
Nested comments ((* a (* b *) *)) | Close the outer comment first, or use // line comments |
Numbers
Section titled “Numbers”- Calculations do not wrap around.
32767 + 1in anINTvariable gives32768, not-32768. Numbers and start values are not range-checked either, sox : INT := 40000;is accepted. Keep your values in range. - Bit operations use the real width.
AND,OR,XOR,NOT,SHL,SHR,ROLandRORwork on 16 bits forINTand 32 bits forDINT. The width comes from the values you combine, not from the variable that receives the result. - Shifting.
SHRshifts in zeros. Shifting by the full width or more gives 0.ROLandRORrotate by the number of bits modulo the width. A negative number of bits stops the PLC with the status error, like a division by zero. - Division. A zero divisor stops the PLC with error. In a start value or constant it is a compile error.
Function blocks
Section titled “Function blocks”| Block | Inputs → outputs | What it does |
|---|---|---|
| TON | IN, PT → Q, ET | On-delay: Q turns on after IN has been on for PT |
| TOF | IN, PT → Q, ET | Off-delay: Q turns off PT after IN turns off |
| TP | IN, PT → Q, ET | Pulse of length PT on a rising edge of IN |
| CTU | CU, R, PV → Q, CV | Counts up on each rising edge of CU; Q when CV ≥ PV |
| CTD | CD, LD, PV → Q, CV | Counts down from PV; Q when CV ≤ 0 |
| CTUD | CU, CD, R, LD, PV → QU, QD, CV | Up/down counter |
| R_TRIG / F_TRIG | CLK → Q | Q for one scan on a rising / falling edge |
| RS / SR | S, R1 → Q1 / S1, R → Q1 | Reset-dominant / set-dominant flip-flop |
Timers run on simulation time: when you pause the simulation, timers pause too.
Besides these standard blocks you can write your own function blocks (Function Blocks & Libraries) and use the PLCopen motion blocks MC_Power, MC_MoveAbsolute, MC_MoveLinearAbsolute and others to move axes and Cartesian groups with jerk-limited profiles (PLCopen Motion). Programs with MC_ blocks need continuous simulation; they are not DES-suitable.
How a scan works
Section titled “How a scan works”The PLC scans once per simulation tick (60 times per second). Each scan reads all inputs at once, runs the program from top to bottom, then writes all outputs together. This works like the process image of a real PLC. Outputs act on the drives in the same tick.
Cold start, warm start and start values
Section titled “Cold start, warm start and start values”| What you do | Start | Variables | Timers and counters | RV_FirstScan |
|---|---|---|---|---|
| Deploy | Cold | Back to their start values | New, with their start inputs | TRUE in the first scan |
| Reset, or resetting the simulation | Cold | Back to their start values | Back to their start inputs | TRUE in the first scan afterwards |
| Run after an error | Cold | Back to their start values | New | TRUE in the first scan |
| Stop, then Run | Warm | Keep their values | Keep their state | stays FALSE |
A variable without a start value begins with FALSE or 0. RV_FirstScan is TRUE in exactly one scan after every cold start, so you can run set-up code once:
PROGRAM MainVAR_EXTERNAL RV_FirstScan : BOOL; PartPresent : BOOL; (* @signal: SensorInFeed *) Conveyor : BOOL; (* @signal: ConveyorStart *) BatchFull : BOOL; (* @signal: SignalTower_Yellow *)END_VARVAR CONSTANT BATCH : INT := 10; (* parts per batch *)END_VARVAR starts : INT := 0; (* counts cold starts *) parts : INT := 0; hold : TON := (PT := T#2s); (* start value for the input PT *) edge : R_TRIG;END_VAR IF RV_FirstScan THEN starts := starts + 1; END_IF; edge(CLK := PartPresent); IF edge.Q THEN parts := parts + 1; END_IF; hold(IN := parts >= BATCH); (* PT keeps its start value of 2 s *) BatchFull := hold.Q; Conveyor := NOT BatchFull;END_PROGRAMRV_FirstScan is not a signal. Declare it in VAR_EXTERNAL like RV_SimulationMode; writing to it stops the deploy with an error. The watch list shows the start inputs of timers and counters as well, for example hold.PT.
Resetting the simulation resets every program’s timers, counters and memory. It also restores outputs to their start values: the values they had when the model was loaded.
If a scan runs too long (more than 200 ms, for example an endless loop), uses too much memory or hits an error such as a division by zero, the PLC stops with the status error. Fix the program and click Run again; the PLC restarts with fresh values.
Writing ST for DES
Section titled “Writing ST for DES”In discrete-event simulation (DES), write logic that waits for a signal or a timer and then settles: another scan with unchanged inputs leaves the same state.
| Continuous simulation | DES (event-driven) | |
|---|---|---|
| When a program scans | Once per simulation tick | On start, when a signal it reads changes, at a timer deadline, and again at the same time after its own change |
| Built-in and your own functions | Supported | Supported, same results (ST Functions) |
| Standard and your own function blocks | Supported | Supported if their state settles (Function Blocks & Libraries) |
PLCopen MC_ blocks | Supported | Not supported: rule D5, the program goes into error (PLCopen Motion) |
| DES check (D1–D5) | Not applicable | D1, D2 and D5 make a program not DES-ready; D3 and D4 are hints |
| Experiment batches | Not applicable | Refuse a model with a program that is not DES-ready |
When a scan runs
Section titled “When a scan runs”In event-driven DES, your program scans when it starts, after a cold reset, when a signal it reads changes, or when one of its timers reaches a deadline. A write-only signal does not wake it. If a scan changes its memory, a function block’s state or an output it reads, it scans again at the same simulated time. Other programs that read a changed output also wake. Programs run in their configured order, once per round, until the state is stable.
The limit is 64 rounds at one time. If the state keeps changing, the affected programs enter error and Problems reports des-settle-overflow. The scan watchdog still limits time spent inside a single scan. RV_FirstScan is true only in the first scan after a cold start, not at every event.
Signal writes reach each program in order. Here, batch means a setMany write is seen as its end state: all values in that write arrive together, and only the last value for each signal is visible. Separate writes can cause separate scans, even at the same simulated time.
The examples below are program fragments. Put the declarations in your program’s variable blocks and the statements in its scan body.
Count edges, not scans
Section titled “Count edges, not scans”Change a counter on an edge or a step change. A level condition can remain true for several scans at the same time.
Bad: counts every scan while a part remains at the sensor.
IF PartPresent THEN cnt := cnt + 1; END_IF;Good: counts each arriving part once.
VAR_EXTERNAL PartPresent : BOOL; ResetBatch : BOOL;END_VARVAR edge : R_TRIG; parts : CTU; cnt : INT;END_VARedge(CLK := PartPresent);parts(CU := edge.Q, R := ResetBatch, PV := 10);cnt := parts.CV;A timer’s Q is also a level. Use R_TRIG on it, or reset the same timer with IN := FALSE on every path through the counting branch. A step guard also protects a counter when every path after the increment leaves that step. You can use RV_FirstScan for one-time initialization. A stable self-hold such as motor := start OR (motor AND NOT stop) is allowed.
Measure time with timers
Section titled “Measure time with timers”Use TON, TOF or TP for elapsed simulation time. Scans per second are no measure of time in DES.
Bad: assumes 120 scans mean two seconds.
IF Enabled AND waitScans < 120 THEN waitScans := waitScans + 1;END_IF;Ready := waitScans >= 120;Good: waits two simulated seconds.
VAR_EXTERNAL Enabled : BOOL; Ready : BOOL;END_VARVAR delay : TON;END_VARdelay(IN := Enabled, PT := T#2s);Ready := delay.Q;Wait between scans
Section titled “Wait between scans”A sensor cannot change while a scan waits inside a loop. Use a step chain that returns control and resumes when the input changes. Loops for calculations are fine when their own body advances the exit condition.
Bad: waits for the conveyor sensor inside one scan.
WHILE NOT SensorAtStop DO Conveyor := TRUE;END_WHILE;Good: holds the conveyor on until the sensor arrives.
VAR_EXTERNAL SensorAtStop : BOOL; Conveyor : BOOL;END_VARVAR step : INT := 10;END_VARCASE step OF 10: Conveyor := TRUE; IF SensorAtStop THEN Conveyor := FALSE; step := 20; END_IF; 20: Conveyor := FALSE;END_CASE;Hold commands until feedback arrives
Section titled “Hold commands until feedback arrives”For a level-controlled actuator, keep the command active until its feedback confirms the movement. Advancing to the next step does not guarantee that simulated time passes.
Bad: clears the command in the next scan, which can occur at the same time.
CASE step OF 10: Extend := TRUE; step := 20; 20: Extend := FALSE; IF IsExtended THEN step := 30; END_IF;END_CASE;Good: keeps the command active until the cylinder reaches its end position.
VAR_EXTERNAL Extend : BOOL; IsExtended : BOOL;END_VARVAR step : INT := 10;END_VARCASE step OF 10: Extend := TRUE; IF IsExtended THEN Extend := FALSE; step := 30; END_IF; 30: Extend := FALSE;END_CASE;Use a second timer for an intermediate deadline
Section titled “Use a second timer for an intermediate deadline”ET updates only when its timer is evaluated at an event. Reading ET does not schedule a scan at the threshold you compare it with.
Bad: expects a one-second event from a five-second timer.
dwell(IN := Running, PT := T#5s);Warning := dwell.ET >= T#1s;Good: gives each deadline its own timer.
VAR_EXTERNAL Running : BOOL; Warning : BOOL; Done : BOOL;END_VARVAR warningDelay : TON; dwell : TON;END_VARwarningDelay(IN := Running, PT := T#1s);dwell(IN := Running, PT := T#5s);Warning := warningDelay.Q;Done := dwell.Q;Wait for a signal instead of polling with short timers
Section titled “Wait for a signal instead of polling with short timers”A repeating 20 ms timer creates about 50 timer events per simulated second. Wait directly for a signal level when you need no actual delay.
Bad: repeatedly checks readiness through a timer loop.
CASE step OF 10: poll(IN := TRUE, PT := T#20ms); IF poll.Q THEN poll(IN := FALSE); step := 20; END_IF; 20: IF StationReady THEN step := 30; ELSE step := 10; END_IF;END_CASE;Good: resumes when the readiness signal changes.
VAR_EXTERNAL StationReady : BOOL;END_VARVAR step : INT := 10;END_VARCASE step OF 10: IF StationReady THEN step := 30; END_IF;END_CASE;What the editor reports
Section titled “What the editor reports”The editor marks findings as information, separately from compile errors. Every message starts with DES: . D1, D2 and D5 give the program a not DES-ready badge in the status and program list. When you start DES, Problems reports PLC program cannot run on events, naming the program and line. Interactive DES start reports this error without a hard stop; experiment batches refuse the run. D3 and D4 are hints and do not block a run. A program with D5 does not run in DES: it goes into error at its first scan.
The message text below follows the DES: prefix. Placeholders identify your variable, timer or loop; n is the timer preset in milliseconds.
| Rule | Message |
|---|---|
| D1 — state changes on every scan | '<v>' changes on every scan without an edge, timer or step change — never settles in DES. Use R_TRIG, CTU or a timer. |
| D2 — waiting inside a scan | <WHILE|REPEAT> loop condition never changes inside the loop — it waits within one scan and never ends in DES. Use a step chain instead. |
| D3 — elapsed-time read | '<inst>.ET' is only current at event times in DES — compare against a second timer instead. |
| D4 — short timer polling | timer '<inst>' (PT <n> ms) restarts in a step chain without an input condition — costs about <round(1000/n)> events per second in DES. Wait for a signal level instead. |
| D5 — motion block | FB '<inst>' (<type>) requires continuous simulation: PLC motion needs fixed-step integration and is unsuitable for DES. |
D4 checks TON and TP timers with a constant preset below 100 ms, including a preset from the declaration. It looks for IN := TRUE in a CASE step without an additional condition that reads a signal your program does not write, and only reports it when the step chain comes back to that step without a step that waits for a signal. A one-time delay, for example a valve switching time, is not reported.
If you have checked that a flagged statement settles, add (* @des: allow *) on the same line as the assignment or the opening WHILE/REPEAT keyword. It suppresses D1 or D2 for that statement only. It does not suppress D3/D4/D5, change execution or remove the runtime limits. The checker cannot prove that several programs together settle; a step cycle or conflicting programs can still reach the round limit.
Differences from cyclic scanning
Section titled “Differences from cyclic scanning”Step chains can pass through several steps without advancing time. An output set in one scan and cleared in the next can therefore form a zero-time pulse. Signal subscribers can see separate writes; a consumer that only checks the level during a movement tick can miss the pulse. Hold level commands until feedback, and use a timer when a pulse needs a duration.
Between events, timer ET values can stay unchanged and there is no fixed scan rate. Use simulation time, timer outputs and plant feedback to judge progress. Continuous/Live operation keeps cyclic scanning.
Saving and sharing
Section titled “Saving and sharing”Each program is stored in the model, on its PLC Program component. Changes are saved with the model and can be undone. If you cannot write to a project, such as the public demo, use Export to save a .st file. Use Import to load it again later.
A program whose Active field is set starts automatically when the model loads, in every workspace. With Active off, the program only loads into the editor; click Deploy and Run to start it. Programs run in an isolated sandbox inside the browser and can only read and write signals.
See also
Section titled “See also”- Virtual Commissioning — all commissioning functions at a glance
- Signals and Logic — PLC signals and logic steps
- ST Functions — built-in functions for calculations, limits and type conversion
- Function Blocks & Libraries — your own function blocks, shared through PLCLibrary
- PLCopen Motion — MC function blocks for axes and Cartesian paths
- Logic and PLC in DES — logic and ST programs in discrete event simulation
- Signals & Alarms — the Simulation / PLC switch
- Laser Welding Assembly Station — the demo used above
- realvirtual CONNECT — connect a real controller instead